The wall behind the fridge is not subject to 210.52(A) any more than the space for the dishwasher, sink, trash compactor, beverage cooler, or any other appliance.
There's no NEC requirement to place a recep. for the fridge behind it, although it's standard practice to do so. In doing so, it does not serve the c'top, so it doesn't require GFCI protection. If, however, the recep for the fridge does end up over a c'top, then it would be considered as serving that c'top and is required to be GFCI'd.
Try a gander at 210.52(A)(5).
BTW, you may not spend too much time in a hallway, but it is habitable space.
Correct no requirement to put the recpt. behind the frig. Just that the wall space must have one.
Now you will really like this. One behind the stove required.
Again read habitable: http://publicecodes.citation.com/st/oh/st/b4v06/st_oh_st_b4v06_2_sec002.htm?bu=OH-P-2005-000004