Don/Larry
Here is a reference from the 2008 ROC for NFPA-70. I hope this helps.
5-44 Log #2249 NEC-P05 Final Action: Accept
(250.8)
____________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Comment on Proposal No: 5-84
Recommendation: Continue to accept in principle.
Substantiation: The original submitted wording would have prohibited the
use of standard pressure connectors (wire nuts) for use with EGCs, and would
have required the use of ?green? wire nuts for this purpose. The panel should
continue to accept its revised wording as the revised wording makes it very
clear that any listed pressure connector can be used for the connection of
EGCs.
Panel Meeting Action: Accept
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
Campbell
Here is a reference from the 2008 ROC for NFPA-70. I hope this helps.
5-44 Log #2249 NEC-P05 Final Action: Accept
(250.8)
____________________________________________________________
Submitter: Donald A. Ganiere, Ottawa, IL
Comment on Proposal No: 5-84
Recommendation: Continue to accept in principle.
Substantiation: The original submitted wording would have prohibited the
use of standard pressure connectors (wire nuts) for use with EGCs, and would
have required the use of ?green? wire nuts for this purpose. The panel should
continue to accept its revised wording as the revised wording makes it very
clear that any listed pressure connector can be used for the connection of
EGCs.
Panel Meeting Action: Accept
Number Eligible to Vote: 15
Ballot Results: Affirmative: 15
Campbell