Good pointI was going with 680.22(C), The CB is the disconnect, are you considering the cabinet door a permanent barrier?
680.43 Indoor installations shall comply with sections I and II of 680...
also have an issue with 680.43 (A)(1)
I'm probably wrong because of the cabinet door, but it seems a joke to me...
I am finding requirements to have receptacles, switches, the disconnecting means for the pool or spa at least 5 or 6 feet away but nothing that prohibits the panelboard from being that close.
But if the disconnecting means is a breaker in that panel that is not allowed - have to run a line to at least 5 feet away then place the disconnecting means for the spa:huh:
The panelboard cabinet and other metal enclosures would need bonded to the equipotential bonding though.
Correct. But if you run out of the panel to a disconnect five feat away and then back to hot tub everything is hunky dory. Weird isn't it?The disconnect for the spa is in the panel. That is not 5' from the tub
Correct. But if you run out of the panel to a disconnect five feat away and then back to hot tub everything is hunky dory. Weird isn't it?
Exactly what I was trying to point out.Correct. But if you run out of the panel to a disconnect five feat away and then back to hot tub everything is hunky dory. Weird isn't it?
Correct. But if you run out of the panel to a disconnect five feat away and then back to hot tub everything is hunky dory. Weird isn't it?
I was going with 680.22(C), The CB is the disconnect, are you considering the cabinet door a permanent barrier?
680.43 Indoor installations shall comply with sections I and II of 680...
also have an issue with 680.43 (A)(1)
I'm probably wrong because of the cabinet door, but it seems a joke to me...
Couple that with 680.43 (C) ) and I think your concern needs consideration.
680.22 Area Lighting, Receptacles, and Equipment.
(D) Switching Devices. Switching devices shall be located at least 1.5 m (5 ft) horizontally from the inside walls of a pool unless separated from the pool by a solid fence, wall, or other permanent barrier. Alternatively, a switch that is listed as being acceptable for use within 1.5 m (5 ft) shall be permitted.
Edit: Ill bet some of the breakers are SWD
Correct. But if you run out of the panel to a disconnect five feat away and then back to hot tub everything is hunky dory. Weird isn't it?
I don't agree as the breaker in the panel is a disconnect also. You just don't get to decide which one is the disco
I felt the exact same way on this, but then thought about it. If we're considering the Breaker in the panel feeding the disconnect a disconnect also,,,, and the panel was say 50' away and not in sight, we'd never be able to hook up a hot tub.
JAP>
That makes no sense. If the panel is more than 50' away then a disconnect must be installed no less than 5' from the tub. How does that make a hookup impossible. As long as one disconnect meets the criteria then it's not an issue.
If the NEC does not want a disconnect closer than 5' then why do you think a panel would be allowed???. Let's not over think this.
If the NEC does not want a disconnect closer than 5' then why do you think a panel would be allowed???. Let's not over think this.
Well in post #2 you said there was no violation so I guess you think a panel is fine closer than 5' from the Tub.
JAP>