How for can unfused service entrance conductors run inside a building?
I'll bite.tom baker said:How for can unfused service entrance conductors run inside a building?
What are you getting at Tom?(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.
As far as the inspector will let me.tom baker said:How for can unfused service entrance conductors run inside a building?
tom baker said:I am instructing a class and wanted to show how the forum works. In some locations the distance is limited.
Spoken like a true lectrishun.stickboy1375 said:As far as the inspector will let me.
tom baker said:I am instructing a class and wanted to show how the forum works. In some locations the distance is limited.
don_resqcapt19 said:It is my opinion that "nearest" means exactly that....if you go through the wall, the service disconnect must be at the point where the conductors pass through the inside surface of the wall.
JohnJ0906 said:Do you mean that they should enter directly into the disconnect?
peter d said:Generally 10-12 feet is the max allowed here.
stickboy1375 said:Yet we can do circles around the outside of the house... :grin: