winnie said:Something else to consider:
The 'waves' that we are talking about are _not_ actual waves in the wire.
-Jon
Oh, but they are waves. Longitudinal waves. Just like sound waves.
winnie said:Something else to consider:
The 'waves' that we are talking about are _not_ actual waves in the wire.
-Jon
LarryFine said:Let's not totally scare the OP away just yet.
"Eighty-two . . . eighty-two . . . eighty-two; two hundred forty six total." ~ Rainman
K2500 said:I am trying to gain a better understanding of phase angles, like why, when you have 60A per phase, that the sum of a 3 phase 3 wire system is not 180A. Also the word potential and what it means has me confused. While I'm not looking for simple answers, somthing to tecnical could cause my head to explode .
Well, in a manner of speaking, you can store electricity in a system for a short duration: a quarter of a cycle. This is what reactive current does, especially with capacitance.charlie b said:But you cannot store “current” in the same way. Every electron that moves away from the source along one wire will have to make its way back to the source via another wire (or via some other path). There is no place along the circuit that can store the “extra current,” until there is a need for it or until there is another place to store it.
LarryFine said:[....]This is what reactive current does, especially with capacitance.
[...]Also, there's electrostatic charge like a Van de Graff genny.
charlie b said:
For a specific example, suppose at a given moment the current in Phase A is at its maximum value. What is going on in Phases B and C at that same moment is that each has a value of current that is exactly equal to one half the peak value, and the current in each is in the opposite direction as the current in Phase A. Thus, you are adding “peak current” (Phase A) to “negative one half peak current” (Phase B) and again to “negative one half peak current” (Phase C). You can see this if you look at Larry’s sketch of three phase currents as shown in post #10. You can look at any point in time, as shown in that sketch, and see that if you add the values of the three phases, you will get zero.
winnie said:Arguably, there are both examples of how Kirchoff's laws are _approximations_.
Kirchoff's Voltage Law says that if you go around a loop, the total voltages sum to zero. But this is _not_ true if the loop encloses a changing magnetic field.
Kirchoff's Current Law says that the sum of the current flowing into and out of a node must be zero. Again, this is not strictly true, because charge can pile up at a given node (say the dome of a Van de Graff generator)...but only if there is a changing electric field.
Note that this does become a semantics argument; for example the voltage induced in a loop by a changing magnetic field can be accounted for (lumped) into the circuit in a way that makes sense and lets you apply the KVL. See http://ocw.mit.edu/OcwWeb/Physics/8-02Electricity-and-MagnetismSpring2002/VideoLectures/index.htm, I believe lecture #16 for the argument about KVL that I am poorly parroting.
-Jon
Yep!K2500 said:So, If this system was unbalanced.
Ia=61 @ 0
Ib=46 @ -120
Ic=62 @ -240
Then, I would take Ia+(-1/2Ib)+(- 1/2Ic)=In
61-23-31=7
This gives me In=7, or 7A neutral current.
If I just shifted values I would say 11A.
Is there a big flaw in my math?
Smart $ said:Yep!
The values you have given are, or at least assumed to be root mean square (RMS) values. AC current having a sinusoidal waveform when plotted has an RMS value of the peak-to-peak range divided by the square root of 2. We typically use RMS values when discussing AC to liken it to DC effectiveness (and use DC formulas). When plotted, RMS has the effect of chopping off sinusoidal-waveform peaks and putting the area removed into the plains. You end up with two lines parallel to the Time axis (the left-to-right going one) and, for a given current, the upper line would be at positive one-half the RMS value and the lower line would be at negative one-half the RMS value, and the effective current is the relative value between lines, which is the RMS value. The area between the lines is equal to the area between the sinusoidal waveform and any steady state voltage reference (the 0V reference is generally used as such) within the peak-to-peak range.
Thus the error in your math is you are not using instantaneous values.
The correct formula for neutral RMS current is:
In = √(Ia?+ Ib?+Ic??Ia?Ib?Ib?Ic?Ia?Ic)Determining the phase angle of the neutral current is a bit more complex algebraicly.
K2500 said:So, If this system was unbalanced.
K2500 said:Ia=61 @ 0
Ib=46 @ -120
Ic=62 @ -240
-
-
-
-
(etc.)
Is there a big flaw in my math?
charlie b said:
Yes. There is no reason to presume that an unbalanced set of loads would have their phase angles at 0, 120, and 240. They won't be, and thus the rest of your steps are invalid. The formula posted by Smart $$ is valid.
Umm, that woud be zero-crossing-to-peak value. But nonetheless, you are correct in the traditional sense. Yes, I erred in my description, but the reason I put it in those terms is because years ago (more than I care to admit :wink: ) I worked with DC offset voltages (or DC with a ripple) and had to adjust my thinking to match. So to correct my earlier description, the RMS value of a sinusoidal voltage or current is:rattus said:The RMS value of a sinusoidal voltage or current is simply the peak value (not peak to peak) multiplied by 0.707 or divided by sqrt(2).
Not Charlie, but yes, it is possible... but in such a case, the neutral current has to be zero. If there is ever any balancing ["linear"] current on the neutral, no more than one of the connected loads are operating at the base phase angle. The easiest explanation is that any current on a neutral conductor has to have a phase angle. If that current balances three conducting lines of a mwbc, it can only be the inverse phase angle of one line, which would also mean the other two lines' loads are equal to each other but not that of the in-phase the load. In fact, the in-phase load must have a current greater that that required to balance the loads on the other two lines, for if it were less, the neutral current's phase angle would be the same as rather than the inverse of line.rattus said:First off Charlie, it is entirely possible that the load currents are separated by exactly 120 degrees, say in the case of incandescent lights.
Umm, the formula is for a 120? 3? 4W voltage system. I believe it to be impossible to have three equal currents at those angles on 4W mwbc of such a system.Secondly, are you sure that the algebraic formula applies for any set of angles? I think it does not.
It is obvious that three equal currents separated by 120 degrees add to zero.
Now consider three equal currents at 0, 90, and -90 degrees. It is immediately obvious that they do not add to zero. However, the algebraic forumula evaluation yields zero.
Enlighten me if I am wrong.
Smart $ said:Umm, that woud be zero-crossing-to-peak value. But nonetheless, you are correct in the traditional sense. Yes, I erred in my description, but the reason I put it in those terms is because years ago (more than I care to admit :wink: ) I worked with DC offset voltages (or DC with a ripple) and had to adjust my thinking to match. So to correct my earlier description, the RMS value of a sinusoidal voltage or current is:
V~rms = |ΔV ? 2√2|, andHowever, your description will suffice for most.
I~rms = |ΔI ? 2√2|, respectively.
You go right ahead and do that... once again, if you like.rattus said:Of course it will suffice because it is the classic formula for the RMS value of a sinusoidal voltage or current and that is what we are discussing. We should not confuse the issue by using vague notation like delta V, or by using peak to peak values. We should use the simplest notation possible, that is:
Vrms = Vpk x 0.707
Irms = Ipk x 0.707