I have always seen that for a balanced 3-phase delta load the current in the delta windings were always 1.73 times less then the line currents (example of 3-phase motor) Would this multiplier apply to balanced single phase loads as well or just for 3-phase loads, and you always have to do the vector addition for single phase loads?
Yes, the multiplier works for balanced single phase loads.