mbrooke
Batteries Included
- United States
- Technician
I refuse to accept the need for the things you want.
I refuse to believe the fact an item or test procedure exists is a reason to mandate into code
These concepts should be considered and tested before being disregarded. Condemnation without investigation is the highest forum of ignorance.
I am not advocating they be mandated into the code, however further investigation is worthy. The fact so many codes require testing raises a flag. Even bare bone codes that let most anything go require testing. If this method does indeed help with the practical safe guarding of life and property its worth using it field.
Tony asked me the exact same question not more than a couple of weeks ago, he asked I answered and then he asked again in this thread. I am not going to keep answering the same question.
And you still kept insisting they nuisance trip by taking his words out of context despite him saying otherwise. When he kept explaining they do not nuisance trip you simply bailed and then kept posting the same. If you can discredit someone who works with RCDs first hand on a daily basis (as well as knowing others who do the same) while you (probably) have never even seen one in real life clearly speaks for itself. I dont think you are here for an honest debate or discussion. Either that you do not want to admit being wrong.
I did not disagree with that view.
Part of the problem is you make your posts so damn long and covering so many topics in one post makes it very difficult to respond via moble.
My posts were long because the topic being discussed which was (AFCIs).
Perhaps you should do some more self examination.
Please, I am ok. I do not want to be Ego driven, that would be an awful fate. Id rather see the whole picture while knowing where I am wrong and where I am right.
For example, main RCDs you will tell me that the fact they use them in Europe is all the proof we need to justify main or sub main GFP here. That's your proof, that and your personal feelings.
I never said it was all the proof or justification. I brought up main RCDs because they are a cheaper way of providing protection and my intent was to have the concept debated in the forum if its worth or not being considered here as a cost saving alternative. So far I heard two good reasons against them which is what I wanted to see.
When people point out that sub main GFP at the trip levels you advocate would cost the consumers more you simply ignore that or try to say troubleshooting won't be needed.
Again, you keep insisting those trip levels are inadequate to cover your nuisance tripping claim which Tony knows is wrong. Whether we use 50ma of 4 amps, if a fault is on one circuit it will trip the GFP. 8 typical circuits with typical electronics are not likely to ever produce leakage currents over 25ma, so a 50ma RCD will hold just fine and only trip for a fault.
That is not proof of a need for sub main GFP, I know you are sure it is but many of us experienced folks disagree.
It is proof that either testing or some type of GFP is needed. I can buy the arguments a sub main GFP would be to much burden when an issues actually arises, so individual GFCI or GFPE beaker would be the way to go.
But no one can deny new homes (as well as buildings) are being built with wiring errors. 1/2 the AFCI nuisance tripping claims come from GFP, and every one of those homes now has an electrical system thats safer then it would have been without GFP.