Like a MEYERS HUB ?Although the jacket may not qualify as an EGC it still is required to be grounded which means that it needs a proper connector to attach it to the panel enclosure.
Like a MEYERS HUB ?
Like individual MC connectors.
So it can not run through the conduit like it is now
each MC cable would have to be connected separately ?
He could take that 90 and hit a 6x6x4 j-box in the wall. Then run your MC's into that.
312.5(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
That would not be needed, but a proper MC connector is.There will be a connector put on the end of the pipe for the bushing
My Fix any comments welcome
:thumbsup:My Fix any comments welcome
My Fix any comments welcome