Did you happen to read the first 5 pages? (6 pages)Is it me, or did anyone notice phase conductors in conduits are the same?
Last edited:
Did you happen to read the first 5 pages? (6 pages)Is it me, or did anyone notice phase conductors in conduits are the same?
Actually, that is not a violation. See Exception No. 2: Raceways and cables installed into the bottom of open bottom equipment, such as switchboards, motor control centers, and floor or pad-mounted transformers, shall not be required to be mechanically secured to the equipment.. . . the violation I see after you guys brought it up was 300.12. . .