Wow that's crazy you're right it has nothing in there about no joints in a panel. So how can inspectors all collectively enforce this if it's not in the city's NEC ammendments?
Possibly an authority thing, someone (as in a contractors assocation or similar group) needs to step in and keep them in check, otherwise they just continue to be on top of their power trip. Not saying they are all bad inspectors, but they are human and can be wrong without even realizing it.
You can't double up the noodles.
408.41 Grounded Conductor Terminations. Each grounded
conductor shall terminate within the panelboard in an individual
terminal that is not also used for another conductor.
How long has this been a requirement? It used to be done all the time, and I would assume it was allowed. It wasn't until 10-15 years ago that it stopped being allowed here, but I haven't researched existence of the rule in past codes to confirm whether it was always a rule or if there was a change about the time we started getting correction notices for it.
Square D and Cutler Hammer (the brands I have most experience with) have always allowed two 14 or 12 awg conductors in the terminals of the neutral bus. (CH may have even allowed three conductors in some of them from what I recall) 408.41 would prohibit doing that with the grounded conductors but you could still land 2 EGC's there if it were the service equipment, plus they generally use same bars for EGC buses.