What is the danger with this type of installation?
Dennis Alwon said:I guess we are looking at 312.5(C). I have never quite understood this exactly. I would say this is legit if (b) is satisfied. I am not sure if that is penetrating a structural ceiling.
Of course I am not sure (c) or (d) is followed either
Needess to say it is done quite often.
Oh yeah-- minor details....oopsinfinity said:You missed the part about it being surface mounted. A recessed panel does not fall under the exception.
infinity said:Dangers? I see none, the NEC feels differently however.
220/221 said:If a fire starts in the panel it can spread via the conduit to the attic.
infinity said:Dangers? I see none, the NEC feels differently however.
roger said:I agree.
Roger
iwire said:I also agree.
Yeah, kinda no different than the fire traveling through a snap-in bushing into the wall.
Jim W in Tampa said:Use to do this all the time,but it is misuse of male adapter.You will get tagged here.Also see it as a chimney if panel burns
acrwc10 said:Looks more like 2 chimneys in the picture. I don't like it myself, it will put the fire into the inside of the building envelope if it were to have a panel fire. That is assuming the ceiling is closed.