Your designer has found a loophole in the words of the NEC but there is no loophole in the intention -JMO. So maybe a change is needed in this area - and may happen if this becomes a common practice.
The intention of the rules, I believe, is to prevent any individual conductor from experiencing a meaningful overcurrent due to having a lower impedance than its counterpart(s) when the load is at full draw. If following the 'loophole' doesn't possibly result in contributing to such an overcurrent, then it's not really going against the intention. With that said, I'm withholding judgment on said possibility, feeling not very qualified to answer.
Why does it decrease current?
...
PV is something I have not worked with, maybe I am just enough behind because of that and am missing something. I feel I have a good understanting of electrical theory, so maybe you can tell me why current decreases here, I don't see it decreasing, just seeing some of it being displaced or diverted from where it normally may flow.
I think ggunn has something in mind like this...
Let's say you've got two sets of paralleled conductors rated 500A, together carrying a full load of 1000 to a facility.
PV guy comes along and taps one set of them, but the output will not be more than 400A (by code.)
PV system puts out full output, so now you have 400A flowing into the tapped conductors.
Facility still uses 1000A, so now it draws 500A utility power on one set, and 400A PV plus 100A utility on the other.
Therefore...
The current on the utility end of the tapped conductor set
decreased from 500A to 100A.
I realize the actual physics of current flow may not be this simple, but if there's a scenario where there's a meaningful
increase in current over the rating of either set of conductors, I certainly couldn't explain how that'd happen. You can seemingly come up with many scenarios where the current is wildly different in the two sets of conductors (e.g. full PV output, zero load), but at first glance they seem to all involve facility draws below what the service would be rated for, and thus currents well below what the conductors would be rated for.