peter d
- New England
Pass. ......
Pass. ......
So, Peter d , if your job was to inspect electrical installations to conform to the NEC
would you be able to do it ? Or, would you sometimes do it one way and sometimes do it
another way ? Simple question, hard answer. It's an Inspectors job to inspect for code
compliance and submit violations to be corrected, It's an EC job to install the work to the
NEC, It's nobody's job to pick and choose what they think is right or wrong for whatever
reason and install the work the way they choose. That is not the 'real world'.
2-hole conduit straps? Why not? I usually use 1-hole straps, though. Less work.
Depends on my mood and how the rest of the job looks.
I agree the cables not being secured is not a life safety issue but it is a code violation, but i do not see why that would fail on a rough inspection, i would pass the rough and leave a field correction notice at the site and check it at the final, save me a trip and keep the job moving forward
Seriously dude. We are talking about the rest of the country where rational thinking is the rule not union pressure.
If you were an inspector would you fail this?
Yes. On the basis of nm wiring protection, the cable on the right needs a raceway or protective panel cover up to 7' AFF, or the enclosure main disconnect is most likely above the 79" maximum height AFF from the looks of the Seu cabling coming down through the panel (unless this is a MLO setup) that should be a 4-wire hookup. Either one or the other exists for non-compliance. JMO rbj
The first thing you mention is your opinion not NEC.
The second thing you mention is impossible to tell from the picture.
The last thing you mention again can not be determined from the picture.
1. I will retract opinion.
2. On the basis of extrapolation of from picture scale and missing rough framing intent to cover up exposed cabling.
3. I agree without height of the panel AFF and description of brand/type of panel shown is not possible but there is a minimum NEC height requirement that must have been met to install this panel as located. [110.26(E)] Working space headroom. 6"6" min. [240.24] OCPD or [404.8] Switch 79"maximum. AFF. [300.4]Physical Damage Protection 7'/2.1m height
I have done installations that looked the same and luckily for me the inspectors let common sense prevail.