If anyone is wondering, a gooseneck is used on SE cable in lieu of a weatherhead. It's usually made up of tape and paint.
Now that sounds like a quality installation.....
If anyone is wondering, a gooseneck is used on SE cable in lieu of a weatherhead. It's usually made up of tape and paint.
Now that sounds like a quality installation.....
There was time when service installations in this state that were very near the ocean were done this way. Not really sure why. :-?
230.54(C) Service Heads and Goosenecks Above Service-Drop Attachment. Service heads and goosenecks in service-entrance cables shall be located above the point of attachment of the service-drop conductors to the building or other structure.
Exception: Where it is impracticable to locate the service head or gooseneck above the point of attachment, the service head or gooseneck location shall be permitted not farther than 600 mm (24 in.) from the point of attachment.You are also required to meet the serving electric utility's service requirements.
Now that sounds like a quality installation.....
We do not use Service-Entrance cable in my area. Most installations here have the Service Heads at or below the point of attachment with a good size drip loop.
As I read it this Article is dealing with SE cable not a PVC or Rigid riser with individual conductors. Am I wrong on this?
YEP I never have understood, PVC, and SE risers.......JUNKY...wont last over time......Use Rigid or EMT
Sorry, you are wrong. A service head can be used on SE cable, EMT, RMC, IMC, etc. A gooseneck may only be formed on SE cable. They both need drip loops or water will enter the conductors through the interstices, will enter the raceway around the bushed holes in the service head, or both. :smile:. . . As I read it this Article is dealing with SE cable not a PVC or Rigid riser with individual conductors. . .
YEP I never have understood, PVC, and SE risers.......JUNKY...wont last over time......Use Rigid or EMT
YEP I never have understood, PVC, and SE risers.......JUNKY...wont last over time......Use Rigid or EMT
I have never understood people who make blanket statements about wiring methods that work just fine and are in use all over the country.
Uneducated?
Uneducated?
Sorry, you are wrong. A service head can be used on SE cable, EMT, RMC, IMC, etc. A gooseneck may only be formed on SE cable. They both need drip loops or water will enter the conductors through the interstices, will enter the raceway around the bushed holes in the service head, or both. :smile:
YEP I never have understood, PVC, and SE risers.......JUNKY...wont last over time......Use Rigid or EMT
That is really not called for.
... its just frustrating thats all.
its just frustrating thats all.
I agree and understand, I have an SE service and have no problem using NM in non-dwelling units. :smile: