Hello to all. As you can see, I am (Justin) with the manufacturer of PowerBridge. I was alerted of this post and thought I could review our perspective to this question.
I promise I am not here to promote or sell anything, this is a highly respected community of professionals and will act professionally in my replies.
I am here to listen, and clairify claims regarding to PowerBridge. As any manufacture, we respect opinions and AHJ assessments as they have final jurisdiction.
Tom, Thank you for bringing this to discussion.
For those not familiar with PowerBridge, it was created in 2006 as a relocation extension kit to meet code compliancy when installed with jurisdiction approved in-wall building wire and j-boxes to connect a recessed outlet installed behind a wall mounted TV directly wired to a recessed inlet wall plate.
These are not installed to the circuit premise wiring to be energized.
The benefit of this two-part wall plate combination is to allow a cord-set to plug into an external power surge/conditioner device to protect the expensive plasma/LCD TV on the wall where it is not possible to have a full protection component connected.
We were just recently, made aware of this in WA state. Based on article written by Ron Fuller "Electrcial Currents -Dec 2009".
We have never been contacted by Mr. Fuller or any AHJ from the state of Washington with regard to this subjective assessment of the use of a UL listed cord-set supplied in our extension kits. The claim is, the cord-set supplied is somehow used as a substitution for fixed wiring.
NEC 408.4 (1) says that flexible cords and cables must not be used as a substitute for the fixed wiring of a structure.
This is the only basis Mr. Fuller has claimed for all extension kits to not meet WA acceptance.
Our confusion with Mr. Fullers claim, PowerBridge is not installed and not made part of the structure premise wiring in any permanent fixed manor. It does not modify, become part of, or change the existing premise power circuit load rated to plug into the front of the circuit.
The PowerBridge design is specific to allow disconnection of power at both source and appliance INPUT (INLET)
It can be unplugged at any time by user from either end, no different than any cord-set used for an appliance device and called out to conform allowable use within the UL standard for cord-sets.
The supplied cord-set is not attached as a substitute for wiring.
The supplied UL/CSA listed cord-set conforms to energize the appliance to the wall mounted display, not any circuit or structures electrical premise wiring circuit. The PowerBridge does not branch to other outlets or circuits, only the one supplied with the extension kit.
Inside the wall, proper code compliant building wire (ROMEX) NM-type or MC-type and correct j-boxes are to be used for the fixed-direct-wired extension portion of a PowerBridge installation. This is not considered a branch extension as it does not actually branch from the premise wired circuit. It is plugged in, to energize, not hard-wired.
With respect to Mr. Fullers assesment in the state of WA we will soon be in contact with his office to further understand and open communication to the basis of claim.
I invite your comments and understand some of you may not accept what the PowerBridge benefit offers beyond having a receptacle installed direct to the circuit.
Regards, Justin, PowerBridge.