How would you bring romex cables into an outside panel, can you use a pvc nipple if so, where do I find how many fit in a particular size conduit, would I need to derrate them? please help me, pictures are appreciated.
Although many areas allow a short nipple to be used in an exterior panel there is nowhere in the code that allows this. Where I am able I will usually put a short nipple into a JB in the crawl space and strip my wires long enough to enter the exterior panel without splice. If the nipple is less than 2' then no derating is necessary. I usually use a 2" nipple-- sometimes 2 nipples into 2 JB's.
312.5 Cabinets, Cutout Boxes, and Meter Socket Enclosures.
Conductors entering enclosures within the scope of this article shall be protected from abrasion and shall comply with 312.5(A) through (C).
(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
(a) Each cable is fastened within 300 mm (12 in.), measured along the sheath, of the outer end of the raceway.
(b) The raceway extends directly above the enclosure and does not penetrate a structural ceiling.
(c) A fitting is provided on each end of the raceway to protect the cable(s) from abrasion and the fittings remain accessible after installation.
(d) The raceway is sealed or plugged at the outer end using approved means so as to prevent access to the enclosure through the raceway.
(e) The cable sheath is continuous through the raceway and extends into the enclosure beyond the fitting not less than 6 mm (? in.).
(f) The raceway is fastened at its outer end and at other points in accordance with the applicable article.
(g) Where installed as conduit or tubing, the allowable cable fill does not exceed that permitted for complete conduit or tubing systems by Table 1 of Chapter 9 of this Code and all applicable notes thereto.
what is "structural ceiling"? how do I get to the attic space witout going through the ceiling
what would be the logic behind "not less than 450 mm (18 in.) "
You don't have to derate.
Some body correct me if this has changed in 08.
"Structual" supports the building.
If you are outside the house to get in the attic is easy, just up the wall then lb in to the attic.
You don't have to derate.
Some body correct me if this has changed in 08.
6" You can.
I'm still trying to figure what Dennis said no nm in conduit out side:-?
(C) Cables. Where cable is used, each cable shall be secured to the cabinet, cutout box, or meter socket enclosure.
Exception: Cables with entirely nonmetallic sheaths shall be permitted to enter the top of a surface-mounted enclosure through one or more nonflexible raceways not less than 450 mm (18 in.) and not more than 3.0 m (10 ft) in length, provided all of the following conditions are met:
6" You can.
I'm still trying to figure what Dennis said no nm in conduit out side:-?
Is this new in 08?
I thought that was just when useing car flex.
We use two inch nipples out the back of a panel all the time. Just did one today. I squeeze as many wires that will fit in the nipple. If it is less then 18" long and has a bushing on the end,
Although many areas allow a short nipple to be used in an exterior panel there is nowhere in the code that allows this. Where I am able I will usually put a short nipple into a JB in the crawl space and strip my wires long enough to enter the exterior panel without splice. If the nipple is less than 2' then no derating is necessary. I usually use a 2" nipple-- sometimes 2 nipples into 2 JB's.