Minuteman said:See.... I told ya I am a nimwit.
Well,....welcome aboard my friend:wink:
Minuteman said:See.... I told ya I am a nimwit.
One consolation - my wire job is WAY better than if Uncle Jed woulda had Jethro wire it. :grin:Dennis Alwon said:LOL....Don't feel bad I think we all have done it. I see it all over the place without ill effect. Not endorsing it but I do believe it is not code compliant.
Seems like we always end up agreeing on the dummy threads. :roll:76nemo said:Well,....welcome aboard my friend:wink:
Rewire said:Thhn you use the 90C table for Amp rating romex you use the 60C table
That's not how the code works. The NEC is permissive. Unless is says you can't, then you can.Karl H said:I don't see where it's permittted to run NM in a complete raceway.Other than for protection which I assume is a sleeve not a complete run.I'd love some assistance on specific ART.#'s
Karl H said:I don't see where it's permittted to run NM in a complete raceway.Other than for protection which I assume is a sleeve not a complete run.I'd love some assistance on specific ART.#'s
mdshunk said:That's not how the code works. The NEC is permissive. Unless is says you can't, then you can.
Karl H said:I don't see where it's permittted to run NM in a complete raceway.Other than for protection which I assume is a sleeve not a complete run.I'd love some assistance on specific ART.#'s
mdshunk said:The securing is what I see as the possible violation.
334.30 Securing and Supporting.
Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (4? ft) and within 300 mm (12 in.) of every outlet box, junction box, cabinet, or fitting. Flat cables shall not be stapled on edge.
Sections of cable protected from physical damage by raceway shall not be required to be secured within the raceway.
Doesn't 334.30 relieve you of that ?mdshunk said:I think the main time your code pickle when running romex in conduit comes into play is for sleeves out of a box.
Take one typical application; sleeving romex from the floor joist area down to a handy box for unfinished basement switches and receptacles. This is not a true raceway, it is only sleeving for protection. The permissions granted by 358.22 might not come into play, since this is not a raceway. That would be more like a table 9, note 2 sleeve. Romex still has the general requirement to be secured within a certain dimension of the box in this case, since it's in a sleeve and not a raceway, which does not happen with these short sleeves out of boxes. The securing is what I see as the possible violation.
realolman said:I would not pull romex in conduit> Seems like too much trouble and expense.... except for going down a block wall to a switch
Nonmetallic-sheathed cable shall be supported and secured by staples, cable ties, straps, hangers, or similar fittings designed and installed so as not to damage the cable, at intervals not exceeding 1.4 m (4 1/ 2 ft) and within 300 mm (12 in.) of every outlet box, junction box, cabinet, or fitting. Flat cables shall not be stapled on edge.
stickboy1375 said:depends, for guys that dont buy thhn everyday and already stock NM, seems like a logical choice for me...
realolman said:I think I'd go buy a few rolls.:smile:
Does a box connector with a bushing... or maybe just a box connector count? Or does it have to be one of those romex connector / emt things?roger said:Actually Marc, if a fitting is used on the end of the raceway you have fulfilled the requirement.
Roger
realolman said:Does a box connector with a bushing... or maybe just a box connector count? Or does it have to be one of those romex connector / emt things?