stevebea
Senior Member
- Location
- Southeastern PA
I was handed a job folder the other day that has me scratching my head trying to figure out how to do this job and make any coin the way it was priced. A church has a 40 year old 5kw Kohler generator which hasnt run for years. Our salesman gave them a price ( $800 less than we charge for a residental install ) on a 8.5kw Kohler RES with a Kohler RDT transfer switch. This setup is to serve 120 volt loads only. The problem is the building voltage is 208/120 3 phase and the RDT is a residental transfer switch set up for 240 volt. I could get a Kohler 100 amp transfer switch with 208v source sensing but it is $750 more expensive and does not have a loadcenter like the RDT the salesman used in his spread sheet to price the job. I could put a single phase isolation xfmr ahead of the transfer switch but that would be pretty costly. Could I use a buck/boost xfmr? I havent done a site visit yet and dont know the loads but there arent any loads being added and the 5kw took care of the existing load. Any ideas? Thanks.