From NFPA an answer to a request for a Formal Interpretation
From NFPA an answer to a request for a Formal Interpretation
Date: 5/8/09
This replies to your E-mail of requesting information on NFPA 70, National Electrical Code ?, 2008 Edition or NFPA 70 ?.
A revision to the 2008 NEC resulted in a new provision in Section 338.10(B)(4) that required application of the ampacity rule for Type NM cable in Section 334.80 to Type SE cable where it is used as an interior branch circuit or feeder. This provision limited the final load ampacity of the conductor within an SE cable to the 60?C ampacity column. When contrasted to the allowance of Table 310.15(B) (6), this 2008 revision results in larger conductor sizes than would have been required by previous editions of the NEC.
The substantiation supporting these accepted proposals (7-88 and 7-90) cited temperature concerns associated with using Type SE cable as an interior wiring method. Proposal 7-90 cited a 1987 NEMA study in which the effect of embedding a cable in thermal insulation was deleterious to conductor insulation unless the conductor?s ampacity was reduced. There was no data included in either of these proposals indicating that application of Section 310.15(B)(6) to Type SE cable installed as a service or feeder wiring method, in which the conditions of use specified in Table 310.16 were not exceeded, resulted in the cable operating at temperatures exceeding its insulation temperature rating.
This brings us back to the premise of my original response and the decision that has to be made by the AHJ for feeders that ?supply all loads that are part of or associated with the dwelling unit?. One approach would be to use the Type NM cable ampacity requirement, that is now tied to Type SE cable by the revision to Section 338.10(B)(4), for all interior feeder and branch circuit installations without considering the installation conditions. Alternatively, the AHJ could use Section 90.4 and assess the particular installation and make the decision that the conditions of installation are such that application of the ampere ratings specified in Table 310.15(B)(6) does not result in the feeder conductors being exposed to operating temperatures that exceeds the conductor?s insulation temperature rating. If that is the case, the goal of the performance requirement specified by Section 310.10 can be met and the overall safety objective to maintain the integrity of the conductor insulation, by judiciously applying the ampacity and operating temperature requirements that have been cited in this response, can be achieved.
To summarize this, Section 310.10 is the performance requirement that the prescriptive ampacity rules and tables in Articles 310 and 338 are used to satisfy. Because there are some questions related to the revision of 338.10(B) (4) and how that correlates with Section 310.15(B) (6), the use of Section 310.10 can be used as the controlling requirement. Granted, that may not be as cut and dry as what you were hoping to learn, but it does provide a means by which to make a prudent determination that helps ensure conductor insulation integrity. Additionally, the 2011 NEC revision process is underway and the Report on Proposals will be available at the NFPA website around the middle of June. I know that there have been proposals directed to CMP-6 and CMP-7 on Sections 310.15(B) (6) and 338.10(B) (4). I urge you to review these proposals and submit any comments you deem appropriate so that the CMPs have the benefit of your expertise and field experience. The strength of the NEC is the process by which it is developed and you have an opportunity to help make the Code stronger.
Paul Choiniere
NFPA Senior Electrical Specialist
Important notice! This correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide professional consultation or services.