Before it's too late:
Before this thread gets closed again, here are just some of the references provided by mivey. This ought to put the nail in the coffin so to speak!
Alternating Current Machines", Sheldon:
"M-I-C-K-E-Wye", Richard P. Bingham, Dranetz-BMI:
"Navy Electricity and Electronics Training Series-Module 8?Introduction to Amplifiers-NAVEDTRA 14180 pg 1-7":
"Photovoltaic Power Systems and The National Electrical Code", Sandia National Laboratories:
RF/Microwave Circuits lecture on baluns by Dr. Charles Baylis, Ph.D, of USF:
When observing that the four-phase system also had opposing pairs of E and -E as well as jE and -jE, C.P. Steinmetz noted that the four e.m.fs of the quadrature system were in pairs opposite to each other and:
"Differential VNA Measurements...", James R. Andrews, Ph.D, IEEE Fellow, of SPL:
Andrei Grebenikov in "High Frequency Electronics" on Combiners and Couplers:
If the zero ordinates of the two curves coincide, but the positive maximum of one coincides with the negative maximum of the other, as in Fig. 11, then Φ = 180? and the curves are in opposite phase.
A "delta" circuit looks like the delta symbol, which is an equal-sided triangle. There are numerous variations of the delta circuit, such as: grounded deltas (one corner of the triangle is connected to a grounded conductor); open-leg delta (only two elements instead of three are used); or, crazy-leg (where one leg is center-tapped to produce two voltages that 180 degrees out of phase from each other).
One way in which a phase splitter can be made is to use a center-tapped transformer. As you may remember from your study of transformers, when the transformer secondary winding is center-tapped, two equal amplitude signals are produced. These signals will be 180? out of phase with each other. So a transformer with a center-tapped secondary fulfills the definition of a phase splitter.
In a utility connected system or with a 120/240-volt stacked pair of inverters, where the 120 /240-volt power consists of two 120-volt lines that are 180 degrees out of phase, the currents in the common neutral in the multiwire branch circuit are limited to the difference currents from any unbalanced load. If the loads on each of the separate branch circuits were equal, then the currents in the common neutral would be zero.
Baluns are commonly made using the center-tapped transformer below...{illustrates a X1->X2 primary winding and a X3->X4+X5->X6 center-tapped secondary winding}...The center tap (nodes 4,5) is grounded. This provides a 180-degree phase difference between nodes 3 and 6.
C.P. Steinmetz said:...Hence can be produced by two coils in quadrature with each other, analogous as the two-phase system, or ordinary alternating current system, can be produced by one coil.
Figure 2 shows another example of a BALUN. In this case the balanced secondary consists of two identical windings that are connected as a center-tapped secondary. The center tap is usually then connected to the common ground. Coax connectors might now be used for all three terminals. Note that the black dots are polarity indicators for the various transformer windings. With the arrangement shown in Figure 2, one of the secondary outputs is "in-phase" with the input and is thus labeled as the (+), or Non- Inverting output. The other secondary output is "out-of-phase" with the input and is thus labeled as the (-), or Inverting output. There is a 180 degree phase difference between the (+) and (-) outputs.
The main requirements to baluns are to provide an accurate 180-degree phase shift over required frequency bandwidth, with minimum loss and equal balanced impedances.
A wire-wound transformer with a simplified equivalent schematic, shown in Figure 13(a), provides an excellent broadband balun covering in commercial applications frequencies from low kHz to beyond 2 GHz. They are usually realized with a center-tapped winding that provides a short circuit to even-mode (common-mode) signals while having no effect on the differential (odd-mode) signal.