Here try this the SEG is based on Circuit. The Ground for the EGC is based on the OCP.
250.58 is a bigger number.What about 250.6?
250.58 is a bigger number.
Prey, why do you assume that the metal water pipe, structural steel, and listed electrodes would pass a greater current into the earth than the electrodes mentioned in 250.66(A)-(C)?
Prey, why do you assume that the metal water pipe, structural steel, and listed electrodes would pass a greater current into the earth than the electrodes mentioned in 250.66(A)-(C)?
The water pipe bond is not the only illogical part of article 250. If I choose to put ground bushings on my conduits, I have to run a 250-122 sized ground conductor through it to satisfy code, but I don't even need to install a ground conductor at all, otherwise.
Thanks, I have a code book too.
The question remains. I don't see the logic in two 250.66's.
Something like that, yes! Thank you!
George, I remember a few years back reading something about ground rods but I can?t remember where it was published.
I asked this question often when I first started as an apprentice and never got a completely satisfying answer.
I'm in the process of building a class for grounding and bonding. I've reached 250.66 and am having a hard time making sense of why we're allowed to use a reduced GEC for these items.
I realize that a water pipe is commonly interconnected with other services, but I fail to see how that really matters in this section. When you get down to brass tacks, you can use any electrode to interconnect services and unbalanced neutral current would be just as inclined to travel down service A's #6 to a ground rod and return up service B's #6 and overload it.
Thoughts?
I'm in the process of building a class for grounding and bonding. I've reached 250.66 and am having a hard time making sense of why we're allowed to use a reduced GEC for these items.
I realize that a water pipe is commonly interconnected with other services, but I fail to see how that really matters in this section. When you get down to brass tacks, you can use any electrode to interconnect services and unbalanced neutral current would be just as inclined to travel down service A's #6 to a ground rod and return up service B's #6 and overload it.
Thoughts?