Not only do we not get to magnify an existing violation we are not allowed to create one either .. in other words the work I perform today has to meet current code and that code requires that all 125-volt, 15- and 20-ampere receptacles shall be listed tamper-resistant receptacles.
Also (406.3(D)(5))
_______________________________________________________________
Submitter: Bill McGovern, City of Plano
Recommendation: Add new text as follows:
(4) Weather-Resistant Receptacles. Weather-resistant receptacles shall be
provided where replacements are made at receptacle outlets that are required to
be so protected elsewhere in the Code.
Substantiation: Without the requirement for weather-resistant receptacles to be
installed at the time of replacement, ordinary receptacles will be installed and
subjected to the same failures as the receptacles they were replacing in the first
place.
Panel Meeting Action: Accept
Number Eligible to Vote: 11
Ballot Results: Affirmative: 11
________________________________
I think we all agree that the language of the Code is not always understood by all.
apparently the CMP agrees, or at least I can make that assumption reading the history that I have posted. I do not disagree that a replaced receptacle should be TR or WP I just don't think that the current language. (08) is that clear. Keep in mind that you might be replaceing a broken device with a TR in a jurisdiction that has adopted the 08 , and ignore that language in an area that has not adopted the current edition.
I don't get to excited about replacements most installers only have the TR's in the van. (in my area).
Note that this proposal was accepted without modification.