So if you change the service from a 60 to a 200 you would use the old GEC to the waterline?
What if it is just a swap out, say 100A for 100A?
So if you change the service from a 60 to a 200 you would use the old GEC to the waterline?
What if it is just a swap out, say 100A for 100A?
I think that will be an AHJ call but if you just changed out the panel I would say that you would not have to redo the gec to within 5'--- I probably would but not sure it can be enforced.What if it is just a swap out, say 100A for 100A?
So if you change the service from a 60 to a 200 you would use the old GEC to the waterline?
I think that will be an AHJ call but if you just changed out the panel I would say that you would not have to redo the gec to within 5'--- I probably would but not sure it can be enforced.
What is upgraing?
Upgrading. But you already knew that.
What is upgraing?
I think that will be an AHJ call but if you just changed out the panel I would say that you would not have to redo the gec to within 5'--- I probably would but not sure it can be enforced.
That show was awesome, thanks for bringing it up!I know, I felt the same way when they cancelled The Fall Guy.
I can't talk anymore, because augie47 said he would ban me.
the question I have to this is what if its an older house with the water pipe grounding at the nearest point, would you now need to run a new grounding wire to within 5' of the water service entrance?
had a phone call while replying didnt see this
my inspectors require the move to water service entrance, was just curious what others thought