residential-05 NEC
customer wants to add a 60A sub to a 200A panel. 200A already has 2 @ 125A subs and 2@ 30A breakers.
do i require load calcs?
thanks!
ya, i guess i can just ask. the problem is they/he would have to calc the whole thing. (which they won't do, at least correctly)
they are only installing 1 20A circuit for lights, plugs. but that leaves alot of open space in the panel.
thanks, you answered my question, basically not much i can do about it!
Why would anyone add a sub panel that uses 2 spaces to add a 1 space circuit ? He admits to adding a load but that load would not count. I suspect he is up to something. Legaly he adds nothing to load calc but then why the sub panel. Your being had big time. Would make note on the paper work / permit that it is passed for purpose of that 1 circuit.
Why would anyone add a sub panel that uses 2 spaces to add a 1 space circuit ? He admits to adding a load but that load would not count. I suspect he is up to something. Legally he adds nothing to load calc but then why the sub panel. Your being had big time. Would make note on the paper work / permit that it is passed for purpose of that 1 circuit.
would What's funny though is that they'll get the permit to put in the subpanel just so they can hook something up to it illegally later.
my thought, too...
i was trying to find a way (calcs?) to put it over 200A and not allow it. i'll make a note and move on...
Jim, no matter what you think of us, you would make a good inspector. :smile: That's the problem, we probably all know that there's more to this than we're being told. What's funny though is that they'll get the permit to put in the subpanel just so they can hook something up to it illegally later.
You would probably be surprised at how little load is actually on that panel if they did a load calc. I have one that's designed for added loads and many a 200 amp panel comes back at less than 100 amps being used, but from time to time I'll get 100 amp panel that calcs out at 102+ amps.
While I agree that they have to potential of overloading the main simply because they have all those subpanels and there for all those spaces that they could use, I've learned my lesson on this forum, you can't inspect for the future.
What would be the worse thing that could happen if they exceeded the current rating of the main breaker? loss of power? now they have to call an electrical contractor to upgrade the service, more work for the contractor seems like a good thing to me. just adding extra spaces IMO shouldn't be a problem. Didn't they remove the number of spaces allowed in a panel box for the 2008 code, so now you're not limited to the 42. Now that I read this forum I stay confused all the time![]()
I gave thought to it few times but would not care to put up with all you inspectors go thru. LOL
What would be the worse thing that could happen if they exceeded the current rating of the main breaker? loss of power? now they have to call an electrical contractor to upgrade the service, more work for the contractor seems like a good thing to me. just adding extra spaces IMO shouldn't be a problem. Didn't they remove the number of spaces allowed in a panel box for the 2008 code, so now you're not limited to the 42. Now that I read this forum I stay confused all the time![]()
No problem with you having a panel with 40 plus spaces and only a few used. Not much an inspector could or would say. But if you then add a sub panel and say its for 1 lighting circuit your simply playing a game. See this all the time, nothing but warehouse with few lights and get CO then build out unit with no permits or inspections.
That is usually the way it is in commercial spaces. The contractor hired by the landlord for the "shell" may not be the same as the one doing the build-out. Not much you can do even if planned that way. The only choice is to be a cop and drive around looking for violaters.
my thought, too...
i was trying to find a way (calcs?) to put it over 200A and not allow it. i'll make a note and move on...