- Lockport, IL
- Retired Electrical Engineer
Before I try to talk a client out of their requested design change, can I get some opinions on which of the following two options is cheaper (including materials and labor)?
Situation: Lab building with four stories above ground level. Main communications room (MDF) is on the ground level. A separate, smaller communications room (IDF) is on each of floors 1 - 4. Each IDF will require seven branch circuits to supply the equipment racks. All four IDFs are located in a vertical line, one above the other, and there is a dedicated chase for the conduit runs.
Option 1: Run all 28 branch circuits (7 per floor, 4 floors) from a panel in the MDF.
Option 2: Run four feeders from the MDF panel to supply four 12-circuit branch panels, one on each floor. Run the branch circuits within each IDF from the panel in the IDF.