Ok i have a MCC that an engineer directed my company to feed a 120/208 3p 4 wire panel from. pulled the wire today and went to terminate and discovered that there is no neutral. Does anyone have any brilliant idea to make this work. Would a isolation transformer do it?
 

raider1

Senior Member
Staff member
Location
Logan, Utah
Yes, you could install a delta to wye transformer and create a grounded conductor, or if it is possible see if you can run a neutral in the feeder to the MCC.

Chris
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Its' "above my pay grade" but there's a transformer configuration called a "zig-zag" that I've been told can do this more economically than a full size power transformer. Perhaps one of the transformer gurus here will expand on this. If not you might mention that to a transformer rep.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
does anyone know of a 208v delta to 208 y is this even possible

Absolutely, any transformer manufacturer can accommodate you, just tell them what you want.

These are actually catalog items.

Roger
 

nakulak

Senior Member
are you sure that what you have is a delta configuration ? it may be that you simply need to pull in a grounded conductor from the source ? (rather than create a new SDS just to get a neutral that is already there) perhaps a little more information would be helpful.
 

nakulak

Senior Member
did they pull a ground and is it metallic conduit ? (ie can you reidentify the gound as a neutral and use the conduit as ground ?)
 

shaw0486

Senior Member
Location
baltimore
if it is 3 phase 208 no neutral i can use a delta wye even if the service coming in to the basement of the building is wye transformer right?
 