Does this Fitting Require a Bushing?
Learn the NEC with Mike Holt now!
  • This meets the NEC requirement for installation
    Votes: 55 51.9%
  • This does not meet the NEC requirement for installation
    Votes: 14 13.2%
  • This conforms to UL listing requirements
    Votes: 7 6.6%
  • I am not sure about the UL listing requirements
    Votes: 3 2.8%
  • I would use a bushing anyway
    Votes: 35 33.0%
  • I always install it this way
    Votes: 14 13.2%
  • Total voters
    106
This is a standard fitting used in the industry where SE cable is installed.
My question is, does the fitting as seen in the picture require a bushing to protect the cable from abrasion?
As long as the sheath of the SER protrudes through the connector as shown, I don't see any need for a bushing.
In that picture I would say that a fitting is not required. Section 300.4 (G) states that a fitting is required if the conductors are not separated from the fitting or raceway by substantial insulating material that is securely fastened in place. IMO the outer sheathing of the cable is substantial insulating material and is securely fastened in place.
300.4(G) is a requirement for raceways, this is an SE cable.
I agree that the SE cable is not referred to in this section I was using it as a guideline. It's a section that mentions an insulated fitting for #4AWG or larger. When I look at the picture the SE cable is larger than #4AWG I thought that was what you were looking for. If not the picture could have been a 14-2 nm cable entering a cable conn and the same question could have been asked.
I agree with this statement.
I do not disagree that one could try to use this for guidance, but the section specifically mentions Raceways.
I'd use the quality of workmanship rule here. In your picture it looks to me like the edge of the throat has been smoothed and is unlikely to damage the conductors or sheath so I say no bushing required. Had the throat been rough then good workmanship would dictate a bushing.
I voted that it does not but only because I thought that it was a Romex type connector which would have a clamp to hold the cable. If it is not a Romex type connector then my answer may be different.
