There are more reasons for the need of a bushing with PVC than first meets the eye. Take for instance the temperature rating of the PVC itself, it is not rated as high as some would think.
From Carlon's website.
" Does Carlon manufacture 105 C schedule 40 PVC?
We do not."
Take a look at this picture. You will see that the installation of the conductors has burned through the fitting. The bushings have a higher temperature, which reduces the damage that may be caused by just such an installation.
We all know just how sharp some of the 'burn-thru' situations just like the picture shows, can be. Hence the CMP has decided that bushings for PVC installations are a requirement.