I will volunteer to run a separate ground conductor thru all runs of emt as soon as the poco's of this country run a separate ground conductor with all their service drops....... We could save some cows lives with that one...
steve
I do, unless it's specified and paid for.Just out of curiosity, how many of us do omit the wire EGC when using metallic conduit?
I've seen that, too. Ocer-tighten a bulb, and the screw-shell pops off the rivet that connects it to the white-wire terminal.Somewhere out there is an electrician that can screw up the installation of an incandescent light bulb.
Sorry, I meant RMC.
Not me........![]()
Actually, installing a nonmetallic box would generally also be a violation of 314.3.The only problem I see is that the EMT raceway's fault path could be compromised with a loose set screw or locknut or if a metallic box in the middle of the run was replaced with a non metallic box after the fact (a long shot, I know, but it could happen).
Jedi mind trick.I did want to make a comment however on a statement larry made and I dont remember which it was.
I have no problem with that, as long as it was bid and paid for, as I mentioned.95% of the Electrical Engineers are going to spec an EGC even with metal conduit. When I am doing plan review, if they call for it then it better be there or it is rejected in the field.....I have had electricians in an effort to save a buck choose to not run it when the engineer called for it and we have no choice but to fail it.
Using the EMT as the EGC is minimum code compliance,but IMO is
poor design. I don't think there are any "experienced" service guys
that hasn't seen hundreds of loose fittings,lock-nuts, or pipes pulled
from their fittings when the EMT was used as the EGC. It's all about
safety. My experience tells me to "Pull a Green with Everything."
Sure you could argue loose splices,bonding screws,etc. Then you still
have the EMT to carry the fault current. If you have loose splices and
separated pipe, well , then it looks like your gonna have a bad day if
you decided to work energized on this hack job of a pipe run.![]()
And IMO that is a poor excuse for adding a cost to a job. Poor workmanship can screw up anything, as previously stated.
Look at it this way there is another conductor and the electrician says grounded conductor, grounding conductor which is which, oh I'll land them both here with all the white wires. AND WE SEE THIS ALL THE TIME. One less conductor for a misapplication screw up.
But does that mean the redundant EGC is only required to be in the patient care area, or once the AC or EMT exits the area (into the suspended ceiling and back to the panel) can the redundant EGC be omitted?
could either be considered
a superior practice,
or a waste of material.
... Are the requirements of 517.13(A) and (B) such that an insulated EGC is required all the way back to the panel, through the EMT, ...
Obviously, there are exceptions to the rule, which is why I used the term "generally." I do not have an SOP for dealing with this code.You do allow for except (1) and (2), right?
Jedi mind trick.