Suppose you were changing panels in an apartment project and found a 14/2 homerun to a living room that apparently was damaged thirty years ago during construction.
The jumper between the neutrals and the load-side EGCs must be intact for the lights to come on.
So, presented with this information, and knowing that correcting the wiring is outside of my scope of work (I pitched in twenty minutes for free), what would you do?
- The black is cut off at the NM connector
- The white is being used as the ungrounded conductor
- The bare is being used as the grounded conductor
- The white has a decent resistance to the bare conductor in the same cable
- The black has no continuity between the panel and the presumed homerun location
The jumper between the neutrals and the load-side EGCs must be intact for the lights to come on.
So, presented with this information, and knowing that correcting the wiring is outside of my scope of work (I pitched in twenty minutes for free), what would you do?
- Hook it back up the way it was, and advise the owner?
- Leave the living room disconnected until advising the owner?
- Hook it back up on a GFCI breaker, and advise the owner?
- Option D?