Didn't refresh my browser to see you made this post before my last one.In order for the load to be evenly distributed among the general illumination circuits as required by 210.11(B), which general illumination circuit(s) would supply the show window?
First question, where does it say in 210.11(B) that the loads must be evenly distributed among general lighting load circuits? ...and backing up a little, where does it say the general lighting loads have to be on separate circuits?
What it does say is that loads calculated by floor area must be evenly distributed up to and including the panelboard. It does not say how the branch circuits are to be distributed from the panelboard. Example: Total service GL for 10,000ft? is 30,000VA. The service splits into two subpanels, each covering 5,000ft?. 15,000VA must be distributed to each panelboard for GL purposes. If the GL connected load is less than the calculated load, each panelboard must carry half the connected load, too.