Im preparing for my california exam and I have been running through some practice questions on code. I have come across a question I can not get the right answer for:
A store building measures 60 feet by 80 feet and is supplied by a 120/240 volt, three phase 4 wire delta system; the building has 60 linear feet of show window lighting. Which of the following is the minimum allowable number of 2 wire, 20 amp branch circuits required to supply the continuous general lighting and show window lighting in this building?
A) 7 B) 8 C) 11 D) 14
Per my calculations 16,800 volt amps(with the 125% demand factor included) % 2,400 Watts = 7 Branch Circuits
Am I missing something because the correct answer per the study guide is 14 Branch Circuits? :-?
A store building measures 60 feet by 80 feet and is supplied by a 120/240 volt, three phase 4 wire delta system; the building has 60 linear feet of show window lighting. Which of the following is the minimum allowable number of 2 wire, 20 amp branch circuits required to supply the continuous general lighting and show window lighting in this building?