Scenario:
GC is in a jam, EC got a large $ advance and skipped town. Me and the GC are on business questionable terms, but personally I like the guy.
Job was to install power to a floating dock by coming from the service on the shore through some 3" conduit to the fixed pier that led to the connection to the floating dock. Subpanels (400-amp) are on the floating dock and a feeder going through the 3" conduit was going to feed the subpanels.
To make a long story short (please don't ask too much), the GC wanted to run W cable from the floater, up the bottom of the gangway, through the framing of the fixed pier, to the 3" conduit and through the 3" conduit to the service equipment. The inspector said it would OK.
I told him he better check the diameter of that 350kcmil type W cable because I didn't think it will fit into the 3" conduit, and I was correct on that. Then he came up with the idea that the outer cover of the W cable could be removed and the conductors pulled in the 3" conduit. Here is where I'd like confirmation on whether what I said next is correct.
I said: If the AHJ would allow that, you would have to get a cord grip on the end of the conduit to hold the cable, but I didn't believe it would be a NEC compliant installation because although W cable has a wet rating, I don't believe the conductors inside the W cable are listed or identified on the insulation and to be installed in an underground conduit they would need to be identifed as a type of conductor having a wet rating. Right or wrong?
Thanks,
GC is in a jam, EC got a large $ advance and skipped town. Me and the GC are on business questionable terms, but personally I like the guy.
Job was to install power to a floating dock by coming from the service on the shore through some 3" conduit to the fixed pier that led to the connection to the floating dock. Subpanels (400-amp) are on the floating dock and a feeder going through the 3" conduit was going to feed the subpanels.
To make a long story short (please don't ask too much), the GC wanted to run W cable from the floater, up the bottom of the gangway, through the framing of the fixed pier, to the 3" conduit and through the 3" conduit to the service equipment. The inspector said it would OK.
I told him he better check the diameter of that 350kcmil type W cable because I didn't think it will fit into the 3" conduit, and I was correct on that. Then he came up with the idea that the outer cover of the W cable could be removed and the conductors pulled in the 3" conduit. Here is where I'd like confirmation on whether what I said next is correct.
I said: If the AHJ would allow that, you would have to get a cord grip on the end of the conduit to hold the cable, but I didn't believe it would be a NEC compliant installation because although W cable has a wet rating, I don't believe the conductors inside the W cable are listed or identified on the insulation and to be installed in an underground conduit they would need to be identifed as a type of conductor having a wet rating. Right or wrong?