Jim,
Where in the code does it tell you to measure around a round column? The best you're going to do is 210.52(A)(2) which defines wall space and says "including space measuried around corners". Round columns have no corners.
got a point there
Jim,
Jim,
point to a spot on colum and go either direction horizontal. If it is 24 or more inches to where you started add receptacle. 210.52 does not have an aception to leave it out. Might be useless wall to you but is a wall. If you can't run wire down it then box it out.
NEC selected 24 inches not me.
But nowhere in Article 210 does it instruct you to measure around a round column. The verbiage is specific to measuring around corners. If there are no corners how can it be required?
So, the architecture has to change to suit the wiring?If you can't run wire down it then box it out.
You don't need to be an architect to know the difference between a column and a wall space
IMO it can go either way. I would ask where a column enclosure is defined as a wall. Make them round and avoid the argument completely.
Don't get me wrong. I feel the outlet should be placed there as an end-user convenience, but not because it is code-mandated. It is not code-mandated, because the column is not a wall space.
210.52 (A)(1) Spacing. Receptacles shall be installed such that no point measured horizontally along the floor line in any wall space is more than 1.8 m (6 ft) from a receptacle outlet.
(2) Wall Space. As used in this section, a wall space shall include the following:
(1) Any space 600 mm (2 ft) or more in width (including space measured around corners) and unbroken along the floor line by doorways, fireplaces, and similar openings
A column is not a wall and is therefore not a wall space. If you enclose that column within a framed structure, then it becomes a column within a wall, but not until. The column, by its very nature, constitutes a broken floor line, in that it is freestanding from the wall space of the room.
If you wrap the column in a decorative fascia, it is still just a column. It doesn't become a wall space until it is framed out as a wall, such as is common with a pipe chase adjacent to a column.
You don't need to be an architect to know the difference between a column and a wall space, and a $2 attorney is all it would take to successfully argue the point.
No, Jim, you have a column.Like it or not you have a wall.
And when you do that, you are going around a column.point to a spot on column and go either direction horizontal.
And the answers are, in order:How about a log wall, concrete block wall, pilaster, or column?
- A log WALL is a wall.
- A concrete block WALL is a wall.
- A pilaster is not a wall.
- A column is not a wall.
I have 2 columns in a finished basement, they are 7" X 7" square and 10' from the wall. According to the NEC are receptacles required on the columns?
But we are going to have to wait for the 2014. Sigh.:roll:2011 NEC will now need several definitions added:
If he has 7" X 7" square column he does not need a receptacle.
If he has a 3" round column wrapped with a 7" x 7" wall he needs a receptacle.