Anyone have an pictures of some service mast they have done?
.........
What's going on with the right-hand mast...... about 16" down from the w'head? The lighting reflection makes it look crimped or bent.
Huh! never noticed that! its a weird reflection.
~Matt
Would it be legal to use a piece of 2" IMC to extend my service head above the roof but just run SE cable through the conduit from the service head to the meter can?
what you cant use SE cable for service entrance?
what you cant use SE cable for service entrance?
Not in wet location
what you cant use SE cable for service entrance?
I wouldn't concider it a wet location unless it was under ground.Not in wet location
I wouldn't concider it a wet location unless it was under ground.
Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
what you cant use SE cable for service entrance?
Where is that? SE cable is SOP for many services around here.
Would it be legal to use a piece of 2" IMC to extend my service head above the roof but just run SE cable through the conduit from the service head to the meter can?