Would it be legal to use a piece of 2" IMC to extend my service head above the roof but just run SE cable through the conduit from the service head to the meter can?
 
Would it be legal to use a piece of 2" IMC to extend my service head above the roof but just run SE cable through the conduit from the service head to the meter can?


Here, no. No SE cable.


You'd have to ask your AHJ.
 
I wouldn't concider it a wet location unless it was under ground.

You would be wrong :). It is moot anyway since se cable is legal in wet locations.

Location, Wet. Installations underground or in concrete slabs or masonry in direct contact with the earth; in locations subject to saturation with water or other liquids, such as vehicle washing areas; and in unprotected locations exposed to weather.
 
what you cant use SE cable for service entrance?

Service conductors here are THWN etc. in IMC.

There is something about running unfused, exposed wiring in/on a building that doesn't seem right to us desert dwellers. :roll:
 
Would it be legal to use a piece of 2" IMC to extend my service head above the roof but just run SE cable through the conduit from the service head to the meter can?

For the POCO here, yes. (Although ridgid is used, not IMC)
You need a bushing on the bottom, and the mast needs to be bonded.
 