Pierre C Belarge
- Westchester County, New York
I would like to add this to some peoples thoughts in regards to other receptacles in a kitchen being required to be on a 20 ampere rated circuit.
210.11(C)(1)
Does not state that all receptacles in a kitchen are required to be on a 20 ampere rated branch circuit.
210.52(B)(3) states "additional small-appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1)."
No where do I see that receptacles located in cabinets, wall space above 5-1/2 ft, or part of appliances,have to be installed on a 20 ampere branch circuit.
If the NEC was intent on having other receptacles on a 20 ampere branch circuit, I am sure we would see that stated as so. Similar to the wording used for GFCI requirements of 210.8 & Arc Fault requirements of 210.12(B).
210.11(C)(1)