Well you cannot quote a part of the sentence. Read art.210.52(B)(1)Ok I understand the NO on the arc fault but isn't that outlet part of the "shall serve all wall and floor receptacle outlets?"
(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Where does it state that another outlet cannot be installed. We had a similar argument about dining rooms. Suppose someone installed a window a/c in a dining that required a 15 amp cir. Can you install a dedicated 15 amp cir there????
I feel that once you install the required outlets for the countertop then the 15 amp recep cir. above the counter is okay. Obviously not everyone feels the same.