stuartdmc
Senior Member
- Location
- Newport Beach, Irvine, CA
I need your help. My electrical contractor is trying to size a load center to run several motors.
I'm helping him get through plan check and he doesn't think my calculations are correct.
If you would, and have a second, I have several motors all are 208v 3 phase,
We have 2 @ 70FLA, 5 @ 40FLA 2, @ 20FLA and 2 @ 25FLA.
My question is, I came up with a the total load of 430 amps correct? and therefore the load center shall be a minimum of 500amp panel.
Thanks for you comments.
Stu
I'm helping him get through plan check and he doesn't think my calculations are correct.
If you would, and have a second, I have several motors all are 208v 3 phase,
We have 2 @ 70FLA, 5 @ 40FLA 2, @ 20FLA and 2 @ 25FLA.
My question is, I came up with a the total load of 430 amps correct? and therefore the load center shall be a minimum of 500amp panel.
Thanks for you comments.
Stu