jaylectricity
- Massachusetts
- licensed journeyman electrician
Can't dispute that, but I have seen many fixtures with thermal sleeves on the wires.
The thermal sleeve is to protect the insulation, not the copper.
Protect it from what? External or internal heat?The thermal sleeve is to protect the insulation, not the copper.
External heat, there should be minimal internal heat if the overcurrent protection is working properly.
You are mistaken there.
The filament in an incandescent lamp is typically between 2000 K to 3300 K (about 3100?5400?F) that heat 'conducts' down through the lamp socket and down the socket leads back to the supply conductors.
Think about this. if you had a wire one foot long and you held it at one end between your fingers then I heated the other end to 5000F how hot do you think your end would be?
The rating on the insulation isn't going to protect the copper. The rating is there to protect the insulation so that it doesn't break down when normal heat is applied to it.
Depends on the time and wire area.Think about this. if you had a wire one foot long and you held it at one end between your fingers then I heated the other end to 5000F how hot do you think your end would be?
I do not think anyone has disagreed with that, copper can carry much higher currents then the NEC allows because of that pesky insulation.
Going back to my question about holding the one foot of wire while I heat one end. Would wrapping the conductor with a heat shield make your end colder, the same or hotter?
All I can say is thank you captain obvious. :grin:
	3100-5400?F at the filament and I'm supposed to believe that enough heat conducts through the conductors that a difference in 54?F in the insulation is going to make it OK?
And where exactly do these "supply conductors" begin? 1ft away from the fixture? 3ft? 10ft? 100ft? The entire branch circuit? The service conductors?
Did anyone say that?
If you cannot figure that part out maybe you should stop wiring fixtures.
Less than 5000F. I would be willing to bet the lamp socket never gets much over a couple hundred degrees at the worst.Think about this. if you had a wire one foot long and you held it at one end between your fingers then I heated the other end to 5000F how hot do you think your end would be?