Greeting dear all, My question is regarding to circuit breaker size. I have the following calculation
TOTAL DEMAND LOAD
(KVA) 122.41
25% FUTURE LOAD
(KVA) 30.60
TOTAL LOAD DEMAND LOAD + 25% FUTURE LOAD
(KVA) 153.01
TOTAL CURRENT 231.83 Amp
CIRCUIT BREAKER RATING 231.83 * 1.25 289.79 Amp
STANDARD CIRCUIT BREAKER SIZE 290 Amp
My question is in the above information I have been already asked for 25% future load and I haved added it. So for determining the breaker size. Should I again Multiply the 231.83, which already contains 25% future , by 1.25.
Please advise me soon.