1.25 is assential for Breaker
Hameedulla-Ekhlas
AFG
Greeting dear all, My question is regarding to circuit breaker size. I have the following calculation
TOTAL DEMAND LOAD
(KVA) 122.41
25% FUTURE LOAD
(KVA) 30.60
TOTAL LOAD DEMAND LOAD + 25% FUTURE LOAD
(KVA) 153.01
TOTAL CURRENT 231.83 Amp
CIRCUIT BREAKER RATING 231.83 * 1.25 289.79 Amp
STANDARD CIRCUIT BREAKER SIZE 290 Amp
My question is in the above information I have been already asked for 25% future load and I haved added it. So for determining the breaker size. Should I again Multiply the 231.83, which already contains 25% future , by 1.25.
Please advise me soon.
BR
Hameedullah Ekhlas
Depending on the circuit breaker type, such as standard molded case CB's, you will need the additional 25% on top of your continuous load.
There are CB's that are breakers that are fully rated, but you need to specify that.
Dear Sir,
TOTAL DEMAND LOAD
(KVA) 122.41
25% FUTURE LOAD
(KVA) 30.60
(KVA) 153.01
Line to line voltage in Afghanistan is 380 and line to neutral voltage is 220 volt.
Hope your question is solved
My opinion would be that if your "demand load" and "future load" is not continuous then you don't need the 1.25 on either. To me the number would be 153.01 if you wanted to add a "future load"
It is a residential load and contains receptacles lighting and etc. So, I applied the NEC demand factor, which is give for receptcles and lighting, and I got the total.
best regards,
Hameedullah Ekhlas
best regards,
Hameedullah Ekhlas
If you used section 220 to calculate the load in the residence, you would not add 25%. In the US you would then take the largest motor, usually the A/C unit and add 25% to that load and then include it in the total. So you need to determine if your residence fits this situation. Usually the NEC calculations will allow for additional loads in the future. Let us know what you decide.
In this design's scope of work has asked me to add 25% for future load.
So, for motors I have already consider artical 430.47 and 430.32 and so on.