An A for effort and a red tag too or not
ivsenroute
Florida
Would 110.14(A) be enough to say that this is a non-compliant installation?
Is there a better section to apply IF this is non-compliant?
What about using 310.15 instead?
is that white a #6? It almost looks like it would fit in the hole on the bar.
Looks like they ran out of holes. Not sure why you wouldn't land the #6 in a hole and then do something else with a couple of the other smaller grounds...I personally would double up some of them on the terminal.
Just want to verify what I think I see...he used a Kearney to connect a #6 [?] to a solid [#10, 12?] that he doubled over [so two of these wires actually are under the lug].
If so, certainly 408.41 and the Kearney probably is [usually] not listed for 3 conductors.
I believe the installer was too lazy to do it right, and ended up making it harder.
That #6 will fit the bus hole if you round it smoothly and take the screw out of the hole.
Maybe the installer wants his hackness to be noticed. A cheesy hack would have simply cut some strands off the back side of the conductor and called it a day.
It is a #6 copper
It is a #10 copper bent in half
It is a split-bolt
It is a main panel, not a sub-feed for a disconnect
It is NM cable
It is a neutral for a 50A circuit
I don't remember what it feeds because I took the picture over a year ago
No thoughts on what this would violate?
His Hackness! That's a great name for him!
Looks like he also used the wrong hole for the bonding strap. There is one slightly closer to the ground terminals just above the one he used. He probably drilled his own... he didn't like the factory one. I keep checking the picture to see if the strap popped off the screw yet!
I guess I see it now.
I don't see why this connection was even needed.
The white wire looks like it is long enough, it looks like it was already bent to go into the ground bar.
There are technically three wires under the split bolt. I bet it is only rated for 2 wires.
I am with the others. Turn off the circuit- lift the neutral and put it under the lug. I can't believe the neutral won't fit under that lug.