SITUATION: 2-#2 Phase Conductors, 1 #2 Bare Solid EGC in 2" Underground Sch. 40 PVC.
I was told that installation of the above size EGC (#2 Bare Solid) violates NEC.
Article 250.118 permits bare solid EGC's. Article 250.122 permits EGC's to be sized up the the size of the size of the phase conductors. I sized the EGC for fault carrying on the circuit.
Does Article 310.3 apply to EGC's? Can someone provide me with clarification and direction?
Sincerely,
Michael A. Armentor, P.E.
Illumination and Electrical Facilities Engineer
LaDOTD Bridge Design
1201 Capitol Access Road Rm 609G
Baton Rouge, LA 70802
"Life is a gift to you. The way you live your life is your gift to those who come after. Live it well, enjoy today, and do something fun. Be happy, thankful, and seek God!?
[/COLOR][/I]
I was told that installation of the above size EGC (#2 Bare Solid) violates NEC.
Article 250.118 permits bare solid EGC's. Article 250.122 permits EGC's to be sized up the the size of the size of the phase conductors. I sized the EGC for fault carrying on the circuit.
Does Article 310.3 apply to EGC's? Can someone provide me with clarification and direction?