I've got a GFCI being used as a disconnect for an AC compressor. I'm wondering if this is a code violation or not. I'm thinking it's just more of a design issue and not necessarily a violation, but I figured I'd ask you guys. Thanks in advance. :grin:
There are GFCI receptacles that are switch rated.
P&S makes a dead-front GFCI that is rated for 1? HP.
However, you can't lock it in the open position....................
Check out 430.109. It gives the acceptable types. The list does include a moptor-rated switch that is rated in horsepower. I did not see anything in the NEC that specifically requires the disconnecting means to be lockable. However, I suspect that other rules would bring that into play. In other words, OSHA rules or other applicable rules might require the maintenance person to install a lock, before performing any work. Someone else would have to speak to that point, as it is outside my arena.Does it have to be switch-rated? and Does it have to be able to be locked out? (code-wise).
Why do you want a GFCI on a compressor?
Would it be code compliant if you used a lockable in-use cover?
~Matt
The unit is hard-wired via liquitite to the load side of the GFCI.
The "TEST" and "RESET" buttons on the GFCIs are only intended to check for the proper functioning of the GFCI. They are not intended to be used as "ON/OFF" controls of motors or other loads unless the buttons are specifically marked "ON" and "OFF." Products with "ON" and "OFF" markings have been additionally Listed under Motor Controllers, Mechanically-operated and Solid-state (NMFT).
~Matt
120v compresor, or only opening one conductor?The unit is hard-wired via liquitite to the load side of the GFCI.