IMO, 250.64(B) does not allow FMC as protection for a GEC ?
What if protection isn't required and you just want the FMC for aesthetic value?
I agree but would add that FMC is not prohibited for 4 AWG and larger.
Dave,
FMC and cable armor are not the same item !
If you have a GEC going thru metal raceway then a bonding bushing is required on both ends to avoid the choke effect.
The grounding conductor from building steel is not the GEC.....is it?
Whatever you call it - it is still there and a metallic enclosure around a GEC and should be appropriately installed for being on the GEC.What if protection isn't required and you just want the FMC for aesthetic value?
Because it's seperate from the system conductors feeding the transformer...Educate me please.
SDS...seperately derived system?
They use the building steel as a grounding electrode for the transformer which is a seperately derived system?
The transformers is an SDS because?
Thanks.
Rob I know it is common, I just don't know if that makes it NEC compliant.
I see your point about it being 'required or not' but at the same time the NEC went to the trouble of specifically making a list of acceptable methods.
At best I would say the issue is muddy.
Funny thing that job in the photo was just inspected on Tuesday and passed.
Because it's seperate from the system conductors feeding the transformer... The grounding for that "system" starts there...
I do not doubt it in the least.
I don't think anyone would look at it and think 'Gee that is unsafe and might be an NEC violation.'