Volta
Senior Member
- Location
- Columbus, Ohio
Yes, eventually. The SDS GEC must be connected to the nearest of the Structural Steel Electrode or the Metal Water Pipe Electrode.GEC from 208 volt side connects to GEC on 480 side?
The interior piping is bonded to the electrical system, the electrical system is grounded by the underground metallic water pipe. Subtle difference in practice.Jumpered from the building steel and piping?
I guess I always thought the building steel and metalic piping bonded to the service instead of part of the grounding system.
Similar with the strucural steel.