GG
- Ft.Worth, T.X.
In what year did the NEC make it a requirement to have a main breaker in a residential service panel? I see houses built in the 70's that do not have a main breaker.
Does this inspector have a code reference to back up his "want"?Yes, an inspector here wants homes without a main breaker to have one installed.
As I said earlier, there has to be both a main disconnecting means for the building and overcurrent protection for the panel. One way to achieve both goals is to put a main breaker in the panel. Another is to put an enclosed breaker or fused disconnect ahead of the panel. I suspect that some meter bases have a built in capability to achieve the same goal. Do you know if the particular installation under discussion has any such devices already installed?So in this picture if this was a panel in the garage of a house and it was fed from a meter base outside, the conductors supplying power to the panel do not need to be on a breaker or disco?
Yes, an inspector here wants homes without a main breaker to have one installed. So in this picture if this was a panel in the garage of a house and it was fed from a meter base outside, the conductors supplying power to the panel do not need to be on a breaker or disco?
Uploaded with ImageShack.us
Is the top left breaker a back fed main? I can't zoom in enough. If it's got a hold down kit, then it's legal. If that's not a backfed breaker, they got their inspection with 6 breakers. and added the rest later
The inspector did not quote a code reference, but I see now that 230.70 and 230.71 apply to this panel. This particular installation, and Im guessing the entire neighborhood, has no disconnecting means for the service conductors that enter the panel. Plus the panel has 30 breakers so its well over the 6 breaker limit. My next question would be how long has 230.70 been a requirement in the NEC, and was there even ever a time when the installation I described was legal to install?Does this inspector have a code reference to back up his "want"? As I said earlier, there has to be both a main disconnecting means for the building and overcurrent protection for the panel. One way to achieve both goals is to put a main breaker in the panel. Another is to put an enclosed breaker or fused disconnect ahead of the panel. I suspect that some meter bases have a built in capability to achieve the same goal. Do you know if the particular installation under discussion has any such devices already installed?
By the way, is the house attached to this garage? If not, some additional requirements come into play.
If it has always been a code requiremenet Im trying to figure out how so many homes passed an inspection as I see this quite regularly.
Well with that exception it looks like the panel is good to go as is. Thanks. Thats odd though, it says for existing panelboards. Since a panelboard requires overcurrent protetction would'nt the panel have been a code violation when it was originally installed to now be considered existing and not needing overcurrent protection?Go to the FPN after article 230.71 which will send you to 408.36 and then go to exception No. 2.
Exception No. 2: For existing installations, individual protection for lighting and appliance branch-circuit panelboards shall not be required where such panelboards are used as service equipment in supplying an individual residential occupancy.
1940, guess its been in there a while. I didnt know you could build a house without a permit, when did it become a requiremnet to get a building and electrial permit when doing construction anyway? Im wondering if building permits were required back in the 70's.I just looked in my 1940 NEC Handbook and the rule exists there. Does that help?
How do you know that they were inspected?
Hang on we are not done here.