- New Jersey
- Journeyman Electrician (retired)
Re-idenify the EGC as a neutral and move on.  If this panel had no EGC and you ran a circuit from it would you be testing the continuity of the EMT?
I already disconnected the ground, put a clamp on the EMT and tested it with a megohmeter. I got less than one ohm between the ground wire and the EMT.
Really?
I see he posted one test result.
I believe that was all the testing he needed to do to rule his idea out.
You would???????
FROM THE OP
You are assuming he lifted both ends of the EGC, I do not see that he has said that.
EMT is an acceptable EGC, if I could verify it is continuous I would use it as the EGC and not make a mountain out of a mole hill.
And you know that he disconnected both ends of the EGC how? (Or should I say How????????) :grin:
How would you have tested the electrical continuity of the EMT if you lifted both ends of the EGC first?
300.10 Electrical Continuity of Metal Raceways and Enclosures.
Metal raceways, cable armor, and other metal enclosures for conductors shall be metallically joined together into a continuous electrical conductor and shall be connected to all boxes, fittings, and cabinets so as to provide effective electrical continuity. Unless specifically permitted elsewhere in this Code, raceways and cable assemblies shall be mechanically secured to boxes, fittings, cabinets, and other enclosures.
I haven't double checked the derating allowed on the neutral, but other than this (or even this) can anyone find faults in this solution?
....The neutral only need to be sized for the load that it will carry. With a minimum size according to 250.66 I believe although I am having trouble finding where it says this.
Probably thinking of 215.2(A)(1) referencing 250.122. Always hard for me to find too for some reason.
I assume a #6 min unless OCP is less than 150 amps 250.122(B).
If he can do that he could likely add a ground wire on outside.
I don't mean to side track, but wouldn't running a egc on the outside of the conduit be a violation of 250.134(B) Jim?
NEC 250.134(B) said:By connecting to an equipment grounding conductor contained within the same raceway, cable, or otherwise run with the circuit conductors ...
If your going to do the job why cut corners ? The customer needs a dedicated circuit, it doesn't sound like it's a poor widow that can't afford the work. WHY,WHY,WHY cut corners? I personally don't like EMT as the ground path. Yes it is code compliant, if it is a low resistance path etc etc, but I have come across too many separated ( old ) EMT runs, that were supposed to be the ground path. Go ahead and do a CODE MINIMUM job, it will pass the inspection. Sucks to be your customer.
You really think so after he saved them thousands of dollars?