All true but we do not need to take extra risks....quote]
We take a risk everytime we energize something, plug something in, drill or cut something, use tools or equipment, sometimes when turning something off it is a higher risk than leaving it on.
I feel safer doing most of my work than I do driving with all the other idiots that are on the road.
Your post almost seems contradictory to the point I tried to make. I agree these additional paths provide a lower resistance grounding. That in itself is great.
But as you said, the NEC does not recognize these extra paths as an equipment grounding conductor. Therefore, simply testing with an ohmeter will not verify the continuity of the EMT run.
The run, short of physically testing the mechanical integrity at each joint, would have to be at least visually confirmed for continuity... and I'm not saying one has to inspect every single inch, but at least to a degree of reasonable certainty for the issue at hand.
Here is what could happen in a situation like this. The panel has many runs of emt and it is possable one of them runs is making connection to build steel. That now gives you a path to ground so you get 0 ohms. Now the problem, remodeling for some reason removes that run of emt. Now your run that you thought was grounded just lost its ground.
An ohm meter will not prove you have the ground you think you have. It can prove you do not have connection
And I am sure we have all seen badly made EGC splices so obviously the only safe and practical solution is to pull the service off the building doing away with this dangerous electricity.
I am with iwire on this, if you want to ensure it is safe from all possible electrical hazards turn it off.
There are many other things that can come apart, or otherwise fail, there are users that modify or abuse things and who knows what may happen from this.
My point was that if you have a structure or equipment with a lot of bonded metal paths I don't really care what NEC recognized equipment grounding method you use - from a safety point of view that equipment is inherently grounded very well and it is difficult to make it not grounded.
I pull more equipment grounding conductors through metal raceways than I used to but still feel for the most part is unnecessary. There are times when I have had something like a gas furnace having problems and the heating guy says I need to have a ground wire in the supply conduit to solve this problem. I install the ground wire and his problem does not go away. I understand why he needs a low resistance ground but apparently my raceway was not the problem. I now install the ground to this type of equipment regardless so they do not have to call me back on that.
Most pulled apart fittings I have seen whether the set screw or compression nut was tight or not could have been prevented by properly securing and supporting of the raceway which we all are supposed to do anyhow.
IMO the only good test the ability of a raceway to carry a fault current is to impose fault level current on it. Or at very least any type of load with current levels above the normal current in the contained conductors. The most expensive ohm meter will not tell you what the effects of the high level current will have on a loose fitting. A megohmeter is a high voltage but low current and will pass through this fitting and maybe even give you a good reading if the contact pressure it tight at time of reading. Heating within the loose fitting during a high current event is what is going to change the impedance of this connection.